battery disconnect [RE-wrenches]

Christopher Freitas - OutBack Power cfreitas at outbackpower.com
Tue May 28 13:08:29 EDT 2002


> Does anyone else have a nicer/better solution?

The "anderson" type switches are available with UL recognition but often 
only that means only that the plastic material was tested as suitable 
and maybe a temperature rise test was completed.  It is very different 
than being "listed".  I strongly advise that the battery disconnect 
should be externally accessible in a safe manner to allow shutting down 
in the case of an emergency.  

Check out the OutBack PSR "power system rack" - it will hold up to 
twelve group 31 sealed batteries along with the 175 amp breaker and 
three additional PV disconnect breakers.  This allows all of the DC 
breakers to be grouped togehter and allows disconnection of each PV 
array individually. It works well with the AEI's built in GFP system. 

The PSR is ETL listed as a photovoltaic accessory item under UL1741.  We 
also offer an outdoor kit for the PSR that meets the rain and sprinkler 
test and a siesmic zone 4 kit.  There is an optional mounting bracket 
that allows the AEI multimode to be mounted on the side of the PSR - 
eliminates all wall mounting and the problems with conducting inverter 
noise into the house.  

Christopher Freitas
OutBack Power Systems, Inc.
cfreitas at outbackpower.com  www.outbackpower.com
Tel 360 435 6030  Arlington WA USA

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================




More information about the RE-Wrenches mailing list