SW fault [RE-wrenches]
Matt Lafferty
pvpro at attbi.com
Sat May 11 11:53:26 EDT 2002
Carl:
Is this a single SW system (120 VAC)? If so, it sounds like the set-up is
incorrectly done since it should be looking for 120 VAC nominal, not 240.
Just my two cents based on what I've seen.
-Matt Lafferty
pvpro at attbi.com
----- Original Message -----
From: "Carl Emerson, Free Power Ltd." <freepower at freepower.co.nz>
To: <RE-wrenches at topica.com>
Sent: Friday, May 10, 2002 10:34 PM
Subject: Re: SW fault [RE-wrenches]
> Hi there,
>
> I was out at a site today that has been in flawless service as a 'stand
alone'
> for about 5 years.
>
> The client has just had the grid connected and I programmed the SW for LBX
mode.
>
> When I tested the LBX cutting in I noticed the AC1 meter reading was
'hunting'
> over a wide AC voltage range and not reading the grid volts correctly. It
was
> cycling continually from 175 to 260 volts on a 240 volt system.
>
> Because of this the SW failed to synchronize with the grid and refused to
come
> on charge.
>
> Is this a common fault ?
>
> I noticed the AC2 was also 'hunting' and not giving a stable reading of
the
> generators output. We managed to bet the generator to sync. so that saved
the
> embarrassment of a flat bank.
>
> I would be interested to know what causes this fault if anyone knows.
>
> Thanks
>
> Carl Emerson
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-Wrenches
mailing list