Yes, they want to see the blades however, I'm seeing a lot of flexibility on
the part of PG&E in several territories. They have accepted fused
disconnects and in every case that I had an existing disconnect they
approved it. One was a real antique, at least 50 yo and my inspector said
"well, this is sure not on our list but I'll put it on!" Then added -"they
sure don't make 'em like this anymore"
-jeff
> From the Solar, Wind & Hydro Powered office of:
> Jeff Oldham
> Gaiam- Real Goods & Jade Mountain
> Design & Consulting Group
> 11755 Mid. Mtn. Rd.
> Potter Valley, CA 95469 USA
>
> Ph: 303.222.3814
> Fax: 707.743.1820
>
> www.solardevelopment.com
>
> "When you turn to face the Sun all shadows fall behind you"
> - Old African Proverb
>
-----Original Message-----
From: jberdner at sma-america.com [mailto:jberdner at sma-america.com]
Sent: Tuesday, May 07, 2002 7:44 AM
To: RE-wrenches at topica.com
Subject: RE: utility obfuscation and obstruction [RE-wrenches]
Bob:
Yes, you are corrrect. They want to see the blades.
PG&E has a list of "approved" disconnects on the Enet site.
If you have any questions, or if I can be of any further assistance,
please do not hesitate to contact me.
Best Regards,
John Berdner
SMA America, Inc.
20830 Red Dog Road
Grass Valley, CA 95945
530.273.4895 (voice)
530.274.7271 (fax)
-----Original Message-----
From: Bob Ellison, Alternative Energy Systems [mailto:ellison at gisco.net]
Sent: Tuesday, May 07, 2002 12:13 AM
To: RE-wrenches at topica.com
Subject: RE: utility obfuscation and obstruction [RE-wrenches]
I wonder if by "visible "break" disconnect switch" they are referring to
being able to see the "arms" in the switch be open as opposed to not
being able to see inside a breaker?
If they inspected the systems before turning them on, what do they want
to do, change the rules? If nothing else the original systems should be
grandfathered just like some of the old "purpa" wind systems that are
functioning on grid now but would NEVER pass the new tests.
Oh yeah, I would have some questions........
Bob
RE. Ellison
Supplier of;
Alternative Energy Systems & Supplies
34642 Countryman Road
Theresa, NY. USA
                              13691-2076
-----Original Message-----
From: Jeffrey Wolfe, Global Resources [mailto:global at sover.net]
Sent: Monday, May 06, 2002 10:21 PM
To: 'RE- wrenches at topica.com'
Subject: utility obfuscation and obstruction [RE-wrenches]
Just received a letter today from our local big utility wannabe. Central
Vermont "Public Service" is Vermont's largest utility, but tiny on a
national scale. But they try to be lke the big guys, and aparently take
their cues from the folks at NIMO.
I've installed quite a few systems in their territory, and for the past
two years, I've used the Milbank airconditioning type disconnect as the
"utility accessible, locakable, load break rated, visible break
disconnect switch..." required in the Vermont (and many other) state net
metering regulations.
today, I received a letter from CVPS as follows:
"Dear Mr. Wolfe:
"It has come to my attention that your Company has installed Milbank air
conditioning disconnects in lieu of the required disconnect switch on at
least three Net Metered customers.
"This device is a disconnect NOT a switch. It does not meet the
requirements of VT PSB Rule 5.100 " A utility accessible, locakable,
load break rated, visible break disconnect switch with safe working
clearances is required for all installations.
"We are hereby requesting that the locations in question be retro-fitted
with the correct type of switch as soon as possible.
"If you have any questions, please contact me.
Sincerely,
Allan D. St. Peter, P.E.
Electrical Engineer
Is this utility trying to block RE? or just being safety conscious? The
little Milbank disconnects have been recommended for this service by,
among others, John Wiles. (I spoke with him today, and received a few
pointers for combating this, which I will do.) I'm not sure how
quibbling about the definition of a "swtich" is really helping RE move
forward. It's interesting to note of course, that no code or standard,
to my knowledge, has a clear definition of what a "visible break
disconnect switch" is. According to everything I can read in NEC, the
Milbank fits the description. (As John pointed out, one cannot safely
trust the handle of a safety switch to indicate the open or closed
position. The mechanism CAN break. One must see the contacts, which
requires opening the safety
switch.)
So I've just written notes to the homeowners (who were copied by CVPS on
the above letter) reassuring them that their installation is safe and
code compliant.
We'll fight this. It will be interesting to see if CVPS attempts to
disconnect the customers' systems. They'd either have to pull the meter,
or, shudder, use the Milbank switch.
I'll let you know how we make out. Any contributions to the defense fund
should be kept cold and presented at the MREF.
Jeff
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-Wrenches
mailing list