utility obfuscation and obstruction [RE-wrenches]

jberdner at sma-america.com jberdner at sma-america.com
Tue May 7 10:59:25 EDT 2002


Wrenches:

The disconnect is not a requirement of NEC, UL 1741, or IEEE 929.
When I was at Endecon and did the type testing for PG&E on the original
SW it was the lineman's union wanted the disconnect.
This was the first time any inverter had been type tested so it seemed
reasonable at the time.

Then it was only a lockable disconnect.
Later it evolved into the totally unnecessary and overly expensive
visible blade disconnect we all know and love.

This is required because you just can't be too sure about: 
the code required disconnect on the DC side, 
the UL Listed anti-islanding circuitry, 
the code required ac circuit breaker(s) and;
last but not least, removing the meter are not enough.

Makes perfect sense to me.
They want it to be more expensive to install so less people will do it.
Has nothing to do with technical requirements.

JSB 




-----Original Message-----
From: Jeffrey Wolfe, Global Resources [mailto:global at sover.net] 
Sent: Monday, May 06, 2002 7:59 PM
To: 'RE-wrenches at topica.com'
Subject: RE: utility obfuscation and obstruction [RE-wrenches]


Lawrence,

You're absolutely right. There is NO valid technical reason for the 
disconnect. IEEE 929 proved that once and for all (Utilities or states
are 
"allowed" to adopt the requirement for a disco if "required" for labor
or 
administrative reasons. There are NO technical reasons provided in IEEE
929 
for the disco.)

Question for EVERYONE:

Who knows of a net metering system where the utility has USED the 
disconnect?

Anyone?

There is no evidence of any disconnect ever having been used in VT.

I'd like to know as much detail about any incident if one was
disconnected 
by the utility.

Jeff

On Monday, May 06, 2002 10:42 PM, Lawrence  Elliott 
[SMTP:larry at energyoutfitters.com] wrote:
> Jeffrey.
> Thought you might find it interesting that just a few hours ago I was 
> able to ask one of the officials from a local Muni utility and he said

> point blank that no disconnect of any kind on a grid intertie system 
> is required in their service territory. This either means that the 
> utility is very irresponsible and has no regard for the saftey of 
> their service personel or this requirement by any utility is simply a 
> silly and essentially brain dead attempt at making you life diffucult.
> Personally I don't think this utility disregards safety.
>
> I say challenge this crap with a vigor.
>
> Larry Elliott
> ----- Original Message -----
> From: "Jeffrey Wolfe, Global Resources" <global at sover.net>
> To: "'RE- wrenches at topica.com'" <RE-wrenches at topica.com>
> Sent: Monday, May 06, 2002 7:20 PM
> Subject: utility obfuscation and obstruction [RE-wrenches]
>
>
> > Just received a letter today from our local big utility wannabe.
> Central
> > Vermont "Public Service" is Vermont's largest utility, but tiny on a

> > national scale. But they try to be lke the big guys, and aparently
> take
> > their cues from the folks at NIMO.
> >
> > I've installed quite a few systems in their territory, and for the
> past two
> > years, I've used the Milbank airconditioning type disconnect as the 
> > "utility accessible, locakable, load break rated, visible break
> disconnect
> > switch..." required in the Vermont (and many other) state net 
> > metering regulations.
> >
> > today, I received a letter from CVPS as follows:
> >
> > "Dear Mr. Wolfe:
> >
> > "It has come to my attention that your Company has installed Milbank
> air
> > conditioning disconnects in lieu of the required disconnect switch 
> > on
> at
> > least three Net Metered customers.
> >
> > "This device is a disconnect NOT a switch. It does not meet the 
> > requirements of VT PSB Rule 5.100 " A utility accessible, locakable,
> load
> > break rated, visible break disconnect switch with safe working
> clearances
> > is required for all installations.
> >
> > "We are hereby requesting that the locations in question be
> retro-fitted
> > with the correct type of switch as soon as possible.
> >
> > "If you have any questions, please contact me.
> >
> > Sincerely,
> >
> >
> > Allan D. St. Peter, P.E.
> > Electrical Engineer
> >
> > Is this utility trying to block RE? or just being safety conscious?
> The
> > little Milbank disconnects have been recommended for this service 
> > by,
> among
> > others, John Wiles. (I spoke with him today, and received a few
> pointers
> > for combating this, which I will do.) I'm not sure how quibbling 
> > about
> the
> > definition of a "swtich" is really helping RE move forward. It's 
> > interesting to note of course, that no code or standard, to my
> knowledge,
> > has a clear definition of what a "visible break disconnect switch" 
> > is. According to everything I can read in NEC, the Milbank fits the 
> > description. (As John pointed out, one cannot safely trust the 
> > handle
> of a
> > safety switch to indicate the open or closed position. The mechanism
> CAN
> > break. One must see the contacts, which requires opening the safety
> > switch.)
> >
> > So I've just written notes to the homeowners (who were copied by 
> > CVPS
> on
> > the above letter) reassuring them that their installation is safe 
> > and
> code
> > compliant.
> >
> > We'll fight this. It will be interesting to see if CVPS attempts to 
> > disconnect the customers' systems. They'd either have to pull the
> meter,
> > or, shudder, use the Milbank switch.
> >
> > I'll let you know how we make out. Any contributions to the defense
> fund
> > should be kept cold and presented at the MREF.
> >
> > Jeff
> >
> > - - - -
> > To send a message: RE-wrenches at topica.com
> >
> > Archive of previous messages: 
> > http://www.topica.com/lists/RE-wrenches/
> >
> > List rules & etiquette: 
> > http://www.mrsharkey.com/wrenches/etiquete.htm
> >
> > Check out participant bios: www.mrsharkey.com/wrenches/index.html
> >
> > Hosted by Home Power magazine
> >
> > Moderator: michael.welch at homepower.com
> >
> >
> >
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
> 

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================







More information about the RE-Wrenches mailing list