UL's monopoly [RE-wrenches]
Christopher Freitas - OutBack Power
cfreitas at outbackpower.com
Thu May 2 14:31:11 EDT 2002
Just to clarify my statements - My posting was specifically addressing
the issue of UL being the "only" acceptable product safety listing
agency for PV equipment. We need to, as an industry, encourage
competition and innovation by advocating acceptance of other NRTLs
providing safety listings.
I agree that the UL/IEEE/NEC standards are not perfect, and that it is
certainly better than not having any standard at all. UL is not perfect
either BTW - thousands of people have been killed by UL listed equipment
that was later found to be not that safe - resulting in changes to the
product's design and the applicable UL standard requirements to
"improve" the product's safety. This is the way the real world works -
its not perfect - but given time, it does make the products safer.
Think about UL listed outdoor Christmas lights - indoor type plugs
without strain relief or weatherproofing / thin plastic insulation on
wires / no ground fault protection ... but they are UL listed! I think
that the AC PV modules manufacturers should add a few LEDs around the
frame of the PV module and call it a Christmas decoration instead ... No
ground fault protection required or fancy wire and they could plug into
an outlet! ;)
In my experience, guerilla solar system are installed safely and use
listed components. The reason they are guerrila is because the utility
will not allow or makes it difficult for the system owner to get
approval. The equipment is the same as "approved" systems - which
typically are approved by the utility by the existance of some
additional paperwork. Unsafe guerilla solar systems should not be
tolerated or used as examples of solar power.
The reality is that the utility lineman is exposed to far greater levels
of risk driving his truck around on the job or eating a couple of donuts
each morning than from utility connected PV systems - yet the utility
allows these activities to be unrestricted. The chance of a utility
connected PV inverter (UL, ETL or CSA listed) islanding is extremely
unlikely (if at all possible) regardless of whether the system was
"ordained" by the utility or not.
We can support system safety and be critical of the utilities and UL at
the same time.
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas at outbackpower.com www.outbackpower.com
Tel 360 435 6030 Arlington WA USA
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-Wrenches
mailing list