600 vdc arc testing [RE-wrenches]
William Miller
wrmiller at slonet.org
Wed Jan 23 11:55:04 EST 2002
PV Geeks:
One problem with the ground located combiner is it removes one of the
advantages of the high voltage array--lower wire losses. Now we are
running our power back and forth from the roof through long leads,
increasing I squared R losses and conduit size.
William
At 06:37 PM 1/21/02 +0000, you wrote:
>Also, we passed the UL1077 tests for our 600 vdc six pole circuit
>breaker on Friday. This PV disconnect allows you to connect six 48 vdc
>nominal PV arrays which are then connected in series for high voltage
>(600 vdc max)once the breaker is closed. It can also be used as a normal
>600 vdc disconnect if the poles are connected in series with wire
>jumpers.
>
After the testing of the breaker we drilled out the rivets and examined
>the contacts - very little wear or evidence was visible. We did over
>300 cycles with load on the breaker during the testing - several even
>with short circuits applied.
>
__________________________________________________________________
William Miller
SLO Communications: Communications and Power Systems Consulting
PO Box 50, Santa Margarita, CA 93453
Voice :805-438-5600 Fax: 805-438-4607 VMail: 805-546-4875
email: wrmiller at slonet.org
License No. C-10-773985
_____________________________________________________________
Compatibility:
Word processor: WP7
Spreadsheet: Quatro Pro 7
CAD: Microstation 95, DXF, Visio 4.1T
_____________________________________________________________
"I stand by all the misstatements that I've made." Dan Quayle
__________________________________________________________________
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-Wrenches
mailing list