Detection of ground faults [RE-wrenches]
Drake Chamberlin - Electrical Energy
solar at eagle-access.net
Tue Jan 15 11:28:10 EST 2002
<x-flowed>
At 08:13 AM 01/14/2002 -0800, you wrote:
>On 1/12/02, Graham Owen wrote:
>>Does anyone know of a device available at this time that helps locate
>>ground faults and
>>arc faults?
Why are all these wires getting nicked? This is not normal. Even in a
Romex wired structure with hundreds of runs, it is rare to have even one
wire get penetrated. (When one does, it ain't good).
The best device to identify a shorted wire is a Digital Multi Meter. Use
the continuity function, and test between all the wires and a grounded
object. After testing between the hot, and both neutral and equipment
ground, take the wires loose at both ends of the run, and test between all
of them and ground.
Also, you can test with a Megger or high voltage insulation tester. This
is good to find conditions that might trip an arc fault detector, but might
not trip a breaker. This condition could exist with an over driven staple.
If wires are routinely getting shorted in conduits, it means that the wires
are being pulled in too stressful a manner. Code requires us never to have
more than 360 degrees of bend in a conduit run. Never, ever jerk on a
wire. If it absolutely won't pull, drag it back out of the conduit and add
more lube, or make a new head on the wires (where they hook on to the rope
or fish tape).
I worked on a commercial job in Florida where certain crews had PVC conduit
runs with 450 degrees of bend, pulling 500 kcmil wires through with power
pullers. Even these didn't short out, even though the stress on the
insulation must have been great.
So, I'm a bit confused about all these ground faults.
Best,
Drake
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
</x-flowed>
More information about the RE-Wrenches
mailing list