DC GFCI [RE-wrenches]
Drake Chamberlin - Electrical Energy
solar at eagle-access.net
Sun Jan 13 16:11:28 EST 2002
<x-flowed>
Ground faults are a common reason for service calls in standard electrical
wiring. Almost always the problem is in a box. The only times I've found
it between boxes is when a cable is damaged. This is pretty rare.
I don't think I've ever pulled a shorted wire out of a healthy conduit
run. (Once from rusted & distorted EMT that was buried in the earth) .
Checking continuity between a disconnected wire and ground tells if the
wire has a ground fault. If the wire is bad, and the problem is not in an
accessible location, replace it.
Drake
At 09:54 AM 01/12/2002 -0800, you wrote:
>It appears that GFI's tripping may become one of the most common PV
>service calls and that finding the fault location is difficult (time
>consuming). What we need is a meter or tool that can reliably display
>how many feet from the GFI the fault is located. I am told that some
>homeowners either defeat bathroom circuit GFI's or replace them with
>standard breakers when service calls become a nuisance. I wonder what
>percentage of PV homeowners in the future will eliminate GFI's as the
>least expensive remedy for making systems operational. Does anyone know
>of a device available at this time that helps locate ground faults and
>arc faults?
>
>Graham Owen
>GO Solar
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
</x-flowed>
More information about the RE-Wrenches
mailing list