DC GFCI [RE-wrenches]

Drake Chamberlin - Electrical Energy solar at eagle-access.net
Fri Jan 11 18:44:59 EST 2002


<x-flowed>
At 11:20 PM 01/11/2002 +0000, you wrote:


>The real hazard from a ground fault is not necessarily from the PV
>panels but from the stored energy in the battery and/or capacitors in
>the inverter.  The DC-GFP system will limit the amount of fault current
>that flows from the battery / inverter when the ground fault occurs.

Battery current will blow fuses.

In early inspections, before the DC GFP devices were available, AHJs would 
allow a breaker to be used.  The problem was considered to be, at that 
time, that the short circuit current from an array was not sufficiently 
greater than the charging current to reliably blow a breaker in the event 
of a short.  Batteries, of course, can do that just fine.

All connections to the battery should be protected by current limiting 
overcurrent devices.

Drake

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================


</x-flowed>


More information about the RE-Wrenches mailing list