Hi Drake,
Thanks for the reply.
I've forgotten the exact section that is stated below, could you give me the
section number?
thanks,
jay
Peltz Power
> CODE QUOTE
> (C) Conductors of Different Systems.
> (1) 600 Volts, Nominal, or Less. Conductors of circuits rated 600 volts,
> nominal, or less, ac circuits, and dc circuits shall be permitted to occupy
> the same equipment wiring enclosure, cable, or raceway. All conductors
> shall have an insulation rating equal to at least the maximum circuit
> voltage applied to any conductor within the enclosure, cable, or raceway.
> Exception: For solar photovoltaic systems in accordance with 690.4(B).
> FPN:See 725.55(A) for Class 2 and Class 3 circuit conductors.
- - - -