Ground fault [RE-wrenches]
Allan Sindelar
allan at positiveenergysolar.com
Thu Nov 14 14:27:23 EST 2002
----- Original Message -----
From: "Electrical Energy" <solar at eagle-access.net>
> This is a very informative thread. I noticed on your web site that the
> negative lead measured - 48 volts to ground. Was that after the wire was
> disconnected, or was there a grounding problem?
If these Carrizo modules are set up as Quad-Lams, 48V dc could be VOC on a
24V nominal array, as these Lams are about 6V VOC each. Is it a 24V system?
What are the specifics of the input current and voltage?
(Three in series won't always charge a 12V battery in hot weather, but four
is higher than needed. A Solar Boost lets you harvest that extra voltage--I
have seen a 50% boost in winter on a QL/SB50 setup; the MPPT trim pot was
maxed out.)
As the PV- and B- are isolated from each other at the SB50, a ground fault
could indeed send full array current from PV- through the controller to the
grounded B-, and overcurrent protection wouldn't catch the fault. Rick
Cullen, could this cause the fire?
Allan at Positive Energy
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-Wrenches
mailing list