Here's John Wiles' response to William's question on rack versus module
grounding:
> Allan:
>
> No. This comes up every year. I address it at least once a year in
> Code Corner. I wish more people would read it.
>
> Early in the days of PV (early to mid 1970's), Jet Propulsion Labs,
> Underwriters Laboratories (UL) and the PV module manufacturers
> determined through extensive and widespread testing and field
> experience that it was not possible to obtain adequate module
> grounding through the mounting bolts used to fasten the module frame
> to a grounded mounting structure.
>
> Aluminum oxidizes very easily and quickly. The oxidation is an
> insulator. Anodized modules (brown or other color) are also
> insulated by the anodizing. These insulators are hard to break down
> and hard to stay broken down with normal mechanical fastenings of
> module frames to module racks.
>
> For this reason, UL Standard 1703 requires that a specific grounding
> point be identified and hardware be supplied for each module to
> ensure that the proper grounding is made and maintained. This is
> usually a self tapping screw made of stainless steel that must cut
> 2.5 threads in the aluminum module frame. Some modules have threaded
> stainless steel inserts to meet this requirement. UL tests this
> grounding connection for continuity and voltage drop with current
> injection to all other parts of the module frame and to any other
> exposed metal on the module.
>
> The NEC requires that all equipment be installed in full compliance
> with any instructions or labels furnished with the product. The
> module instructions and the marked green grounding point on the frame
> override any general requirements found in either Article 690 or in
> other sections of the code.
>
> >John, is William correct as you see it?
> >Allan
> >
> >----- Original Message -----
> >From: "William Miller" <wrmiller at slonet.org>
> >
> >Friends:
> >
> >I am researching some new module mounting for rooftops-- more on that
later
> >as it develops. One question pertinent to the design is module frame
> >grounding. One concept I had been wanting to research is that of
grounding
> >only the rack frame. The Code seems to allow this:
> >
> >690.43 Equipment Grounding.
> >Exposed non-current-carrying metal parts of module frames, equipment,
> >and conductor enclosures shall be grounded in
> >accordance with 250.134 or 250.136(A) regardless of voltage.
> >
> >Researching further:
> >
> >250.136 Equipment Considered Effectively Grounded.
> >Under the conditions specified in 250.136(A) and (B), the
> >non-current-carrying
> >metal parts of the equipment shall be considered effectively grounded.
> >(A) Equipment Secured to Grounded Metal Supports. Electrical equipment
> >secured to and in electrical contact with a metal rack or structure
provided
> >for its support and grounded by one of the means indicated in 250.134.
> >The structural metal frame of a building shall not be used as the
required
> >equipment grounding conductor for ac equipment.
> >
> >Therefore, if one grounds a rack frame, the modules being "secured to and
> >in electrical contact with" the racks renders the module frames
> >"effectively grounded".
> >
> >Comments?
> >
> >William Miller
> >
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-Wrenches
mailing list