600 VDC switches [RE-wrenches]
Chris Worcester
chris at solarwindworks.com
Fri Sep 20 11:37:09 EDT 2002
Hi Wrenches,
I have a GE safety switch (model GEDTH2261RDC) rated at 600V DC 30A fused
disconnect to share info on. I was concerned as to it's application as one
pole, out of 3, is jumped to another at the factory, and the 3rd pole is not
jumped. I found 12 Amp 600V DC rated class R fuses that fit. According to
the internal schematic this is a 2 pole, line to load disconnect. Because of
the difference in the way the poles are wired we had a lengthy debate as to
how to use this device at the 600 V rating. I called GE and got through to
an engineer that informed me, after much questioning, that this is a single
circuit disconnect for DC applications, in other words; the positive is
landed on the jumped pole, for a double contact break, and the negative of
the same circuit is landed on the single pole. In this way the single
circuit is opened without a DC arc. I hope this helps.
Chris Worcester
www.solarwindworks.com
chris at solarwindworks.com
Toll Free: 877-682-4503 Fax: 530-582-4603
"Proven energy solutions"
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-Wrenches
mailing list