the insanity of grounding DC side (was Re: DC-GFP/2 protection [RE-wrench

Hugh Piggott hugh.piggott at enterprise.net
Sun Aug 25 17:09:24 EDT 2002


<x-flowed>
At 11:37 am -0700 24/8/02, Todd Cory, Mt. Shasta Energy Services wrote:
>..... all metal chassis etc. need to be grounded so there is no potential
>between that and ground. It does not mean that you should ground one of the 2
>conductors on the DC side.... The potential only is between the 2 conductors
>and thus it is more safe.
>
>The reason why we have a grounded (bonded) conductor (I.E. the white neutral
>wire) system here in the USA, is to justify the use of a third 
>ground wire which
>benefits the wire manufacturers and unions that install them.

How can you ground your equipment without that ground wire?  That 
wire is to prevent any piece of metal around the system from getting 
up to a different potential from any other piece of metal, or from 
ground potential.  It's a good idea.  Prevents shocks.

>  Grounding one of
>the DC conductors does absolutely nothing to make systems any safer and IMO
>makes them much less safe.

If one conductor is grounded, then a fault in the other will 
automatically take out the overcurrent protection (fuse or breaker) 
and remove the supply.  Neat, simple solution.
-- 
Hugh

http://www.scoraigwind.co.uk/

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================


</x-flowed>


More information about the RE-Wrenches mailing list