Steve, Thank you for describing your well-designed system. Your experience is
similar to old-timer wind pioneers. The National Electrical Code is important
and necessary, but dogma requiring everyone to ground the DC negative weakens
the Code's credibility and inhibits "out of the box" thinking. I'll bet if
Benjamin Franklin were alive, he would be experimenting with PV and wind system
grounding instead of following someone else's rules. Franklin was an American
Revolutionary who wasn't afraid to take risks.
"Steve Bell, Sunwize Technologies" wrote:
> Hi Joel, et al,
>
> I live out on the prairie of Illinois and we get some real wrath-of-god
> thunderstorms. I have an old long-case Jacobs on a 115' tower (tallest
> structure within several miles)as well as both a roof-mounted PV array and a
> second array on a tracker. I float my DC wiring completely; it is totally
> ungrounded except for being connected to Delta LA302DC lightning arrestors
> installed at the base of the tower and the combiner boxes of each array. My
> system operates at 48 VDC with dual SW (not stacked) and I sell my excess
> back to the grid.
>
> I have very good grounding on the tower (ground rods on all four guy anchors
> and the base of the tower) and on frames and racks of the PV arrays. I also
> use Delta LA302R arrestors on both the AC input from the grid and the AC at
> the subpanel (AC output of the SW inverters).
>
> We have experienced some severe electrical storms that have caused
> significant damage to my neighbors electrical equipment, but I have not had
> any damage to my equipment. The only lightning damage that I every
> experienced occurred when my system was new and the Delta arrestors were not
> yet installed (they were on backorder). A nearby lightning strike caused a
> huge surge on the utility AC line that blew out the microprocessors of the
> SW. That was about 5 years ago. Since then, no problems.
>
> I have yet to hear a clear technical reason (not just because its code) for
> grounding the DC conductors. I firmly believe that a floating DC system is
> both safer and less prone to lightning damage. I do believe in very good and
> solid chassis/equipment grounds.
>
> So, I would request that the Code Review committee consider removing from
> the 2005 NEC, the requirement to ground DC systems. Or prove with solid
> technical reasons why grounding the DC wiring is requirement for safety. If
> DC systems were allowed to be floating, we could also do away with all the
> silliness and cost and hassle of PVGFP.
>
> Okay, go ahead and blast me.
>
> Sincerely,
> Steve Bell
> Stelle, IL
> sebpv at stelle.net
>
> ----- Original Message -----
> From: "Joel Davidson" <joeldavidson at earthlink.net>
> To: <RE-wrenches at topica.com>
> Sent: Thursday, August 22, 2002 10:53 PM
> Subject: Re: DC-GFP/2 protection [RE-wrenches]
>
> > Jacobs use to float the DC negative on his wind machines to prevent
> lightning
> > damage. He grounded the tower with a ring of copper wire 10 feet out from
> the
> > tower base buried about 18 inches to form a cone of protection. I resisted
> > (pun?) grounding the DC negative for years, but finally gave up. However,
> my
> > systems are almost all in regions with low lightning danger. What say you
> guys
> > in lightning territory?
> >
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-Wrenches
mailing list