SW4024 Battery Charging Question [RE-wrenches]
Bob-O Schultze, Electron Connection
econnect at snowcrest.net
Mon Jun 24 10:32:45 EDT 2002
<x-flowed>
Jeff,
Did you measure the peak to peak ac voltage from the genny while
under that 110A charging load WITH the batteries at 29-30V?
Bob-O
>We recently did a full instrumentation check on an off grid remote
>solar/generator/battery system that uses one Trace SW4024 inverter. House
>electrical loads are very small and no large AC surge loads like pumps or
>HVAC equipment. Anyway, the system has worked great for three years, but
>owner was never able to do an equalize charge on the sixteen (16) L-16
>batteries.
>
>He could never could get the "equalize" mode (generator menu) to work as the
>generator would shut down as soon as he switched to equalize(yes, we know
>about switching out of auto first and how to set up for equalize charge
>later), so we started the generator manually and then switched to equalize
>charge. Charging started ok at about 110 amps at 29 to 30 volts. After one
>and one half hours, the inverter DC charging amps would drop to zero amps
>and the inverter would start using battery amps for about 5 seconds, then
>the charging mode would ramp back up to the 110 amps charging level. This
>10 second cycle would repeat every 2 minutes until the 2 hour bulk setpoint
>was reached, then it switched to float mode charging.
>
>The battery bank was fairly large and in good condition, and all cells were
>close in state of charge. I don't see why the inverter would be "hunting"
>or testing battery condition as the battery was easily taking the full bulk
>charge with very little temperature rise.
>
>Anybody know what's going on ?
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
</x-flowed>
More information about the RE-Wrenches
mailing list