Trace 4000 SW vs. 1HP 220v well pump [RE-wrenches]

Christopher Freitas - OutBack Power cfreitas at outbackpower.com
Fri Jun 14 17:41:22 EDT 2002


> Chris Worcester wrote: What is the surge on the OutBack, anyone know?

The surge on the OutBack X240 autotransformer is limited by the 25 amp 
circuit breaker provided with the transformer.  You can easily trip it 
if the load on the 240 vac side is to large.  This gets tricky when 
using the transformer at 6 kW with the fan - but the breaker we are 
providing in the current production kits is a 100% continuous rated 
hydralic-magnetic breaker - not a thermal square D QOU type (rated at 
80% continuous) type provided with the T240. If you got one of the first 
kits with the QOU breaker let me know and I will upgrade you to the 
Hydralic breaker at no charge.   

The addition of the fan on the x240 (or t240) would improve the 
performance similarly.  Our transformer was tested with and without the 
fan (4 and 6 kW ratings).  

The real issue on "surge" ability with a step up transformer is that 
some voltage drop occurs through it when carrying high currents.  This 
can cause the motor to draw even more power for a longer period of time, 
 which can then cause more voltage drop ... and so on...

The best method for estimating the suitability of an inverter/pump combo 
is to either get the Locked Rotor Amp rating (LRA) from the manufacturer 
or measure it with a Fluke 87 or 89 with a clamp meter if installed.  
The fluke should be used at both 1 mSec and 100 mSec settings and the 
pump should be started several times and the highest number used. 

The SW4000 can provided about 100 amps max for the 1 mSec peak number 
and 78 amps for the 100 mSec RMS number.  The pump needs to draw less 
than this by at least 20% to be safe.  The inverter will surge to lower 
levels when hot (like after battery charging) so even if the pump is 
below the above levels you can run into problems.  

I have also had good success with Allen-Bradley Starting Torque 
Controllers (STCs)in the past to start motors that were not within the 
ability of the SW.  They are made for conveyor belts motors to reduce 
shock loading on start up.  Another option is to parallel or series a 
second SW but that gets expensive and is often difficult to fit unless 
planned for.  

Christopher Freitas
OutBack Power Systems, Inc.
cfreitas at outbackpower.com  www.outbackpower.com
Tel 360 435 6030  Arlington WA USA

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================




More information about the RE-Wrenches mailing list