Hybrid PV/Battery/Generator [RE-wrenches]
Bob-O Schultze, Electron Connection
econnect at snowcrest.net
Fri Jun 14 13:48:11 EDT 2002
<x-flowed>
Ray,
Yep. Allan has it right. I believe it's because transformers work
with the P to P rather than the RMS voltage. If the genny P to P
under load is low you run out of headroom to push amps into the
battery as the battery voltage rises. That's also why HF
switcher-type chargers are far less sensitive to low P to P.
Bob-O
>Ray,
>I think you are correct about RMS-peak ratio. It also correlates with
>Trace's inverter manuals from the late 80's on, that to get full DC output
>from the charger you needed to maintain 164V peak under load. The inverter
>used the peak of the waveform, so a small drop in peak V meant a large drop
>in DC A.
>Allan at Pos E
>
>----- Original Message -----
>From: "Ray Walters" <remotech at taosnm.com>
>I beleive the the ratio for a pure
>> sinewave is rms volts = .707 peak volts. Somebody correct me if I'm
>wrong,
>> but that would put peak volts at about 170 for an rms voltage of 120.
>>
> > Ray
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
</x-flowed>
More information about the RE-Wrenches
mailing list