Connections and Understanding [RE-wrenches]
Matt Lafferty
pvpro at attbi.com
Tue Jun 4 22:35:59 EDT 2002
William:
I have been meaning to respond to this message you posted a while back.
I do not allow unsupported cable on any of my installations. I also don't
allow un-sleeved cables to be run outside the perimeter of the array.
The technique we use is to sleeve the cable(s) with Non-Metallic Liquid
Tight Flexible Conduit (A product that I condemned for many years but find
it to be quite suitable for this application) anywhere it extends beyond the
periphery of the array to a termination point (J-Box/Combiner).
This flex is supported by blocking and secured. It has a normal connector
at the termination point but no connector under the array. We then seal the
"open" end with duct-seal or splicing mastic to prevent critters and/or
moisture from entering.
So far it works well, Homeowners are pleased, Inspectors like it and we have
had no problems with it. I have used this method for about 2-1/2 years (not
the tray cable, but sleeving of USE--2 cables).
In the case you describe, I would probably turn the Module J-boxes toward
one-another so you could run an output to a J-box between every two rows and
connect the J-boxes to the combiner with EMT. Does that make sense? Hope
so. I've had a long day.
Best to all!
-Matt Lafferty
pvpro at attbi.com
William Miller Wrote:
> Friends:
>
> I am a died-in-the-wool conduit user. I have been researching this
concept
> of using tray cable. The samples of tray cable I have seen don't look
that
> robust to me. Maybe I've been sent the wrong samples. They have grooves
on
> the outside of the jacket. How does this seal in a gland connector?
>
> Routing of unprotected wire concerns me most of all, for example: I am
> currently installing a roof-top system in which the modules are in racks
of
> 8, two rows of racks down the length of the roof, modules in strings of 4
> (48 volt system). I have a combiner on the right end of each row of 16
> modules. This means I have 10 leads to gather at the combiner (4
> negatives, 4 positives and two grounding wires). Am I to understand that
I
> would run tray cable, unprotected by conduit, 40 feet from the left most
> module, across the backs of 16 modules, along with the other leads from
the
> modules at the far end of the row, all the way to the combiner? Hey, I'm
> all for keeping costs down, but I've long ago established standards that
> don't allow wire flapping in the breeze. Am I missing some hardware that
> is available to protect, support and make aesthetically pleasing these
tray
> cables? Does anyone have any pictures I could look at of these tray cable
> installations, done well?
>
> If these concerns aren't addressed by the industry, I feel we should
> collectively condemn this wiring method. Unprotected, unsupported wire
is
> the same concept as "knob and tube" wiring.
>
> Still wondering........
>
> William Miller
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-Wrenches
mailing list