Parallel Reality Danger? [RE-wrenches]

Mangelsdorf, Marco mmangelsdorf at hei.com
Sun May 26 13:19:51 EDT 2002


I propose that Ray's conundrum be added to new CA. C-46 licensing exam
with an additional question as well: if a moose chews through an array
wire in the forest, is shocked and faints dead away and there is no one
there to hear the commotion or to see the moose fall, did it really
happen?  Contemplate the sound of one hand clapping....
 
marco
proVision technologies, inc.
hilo, hawai'i
www.provisiontechnologies.com
 

	Hi Bill and all;
	
	Here is another potentially dangerous situation to ponder: a
5amp UL listed
	device (a computer) is powered through 16 awg SJO cord to a 15
amp rated
	receptacle. This receptacle is PARALLELED with several other 15
amp rated
	receptacles (35cents made in China). This whole circuit is fed
through a 20
	amp breaker. Coffee spills on the computer creating a short.
Because of the
	time/ current performance of the breaker, over a hundred amps
could pour
	into our soaked device for a few seconds and  20 amps could flow
	continuously into a device UL listed for only 5.
	Compare this scenario, with my maligned array wiring method: two
array
	strings each having a short circuit output of 4.75 amps and a
series fuse
	rating of 15 amps feed thru 12 awg wire  in parallel for a total
of 9.5
	amps to a 15 amp breaker. A moose chews through the wire
creating a short.
	Up to 15 amps continuous are allowed to backfeed into the
circuit ( the
	charge controller also failed) and are boosted another 4.75 amps
by the
	paralleled string. This time almost 20 amps could possibly (but
not
	probably because of the high resistance) flow into a device UL
listed for
	only 15.
	Why is the first condition allowed, but the second is not? Is
120 vac safer
	than 48 vdc?
	
	Sincerely again,
	
	Ray

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================From ???@??? Sun May 26 11:10:20 2002
X-Persona: <Michael SolarHost>
Received: from outmta004.topica.com [64.125.140.213] by imail.solarhost.com
  (SMTPD32-7.00) id AFD0B80260; Sun, 26 May 2002 13:48:00 -0400
To: RE-wrenches at topica.com
From: Joel Davidson <joeldavidson at earthlink.net>
Subject: Re: Non wrenches [RE-wrenches]
Date: Sun, 26 May 2002 10:34:07 -0700
Message-ID: <0.1300002502.1614249305-1463792638-1022435773 at topica.com>
Errors-To: <list-errors.1300002502.0.1300215577.009.0.0 at boing.topica.com>
Reply-To: RE-wrenches at topica.com
X-Topica-Id: <1022435771.inmta006.4795.1020129>
List-Help: <http://topica.com/lists/RE-wrenches/>
List-Unsubscribe: <mailto:RE-wrenches-unsubscribe at topica.com>
Return-Path: <joeldavidson at earthlink.net>
Received: (qmail 10954 invoked by alias); 26 May 2002 17:56:10 -0000
Received: (qmail 10942 invoked by uid 0); 26 May 2002 17:56:10 -0000
Received: from pa-fey.topica.com (208.184.76.200)
  by inmta006.topica.com with SMTP; 26 May 2002 17:56:10 -0000
Received: from gull.prod.itd.earthlink.net (gull.mail.pas.earthlink.net [207.217.120.84])
	by pa-fey.topica.com (8.12.2/8.12.2) with ESMTP id g4QHZvv5019348
	for <RE-wrenches at topica.com>; Sun, 26 May 2002 10:35:57 -0700 (PDT)
Received: from pool0851.cvx17-bradley.dialup.earthlink.net ([209.179.235.86] helo=earthlink.net)
	by gull.prod.itd.earthlink.net with esmtp (Exim 3.33 #2)
	id 17C1u0-0001mT-00
	for RE-wrenches at topica.com; Sun, 26 May 2002 10:33:57 -0700
X-Mailer: Mozilla 4.75 [en] (Win98; U)
X-Accept-Language: en,zh-TW
MIME-Version: 1.0
References: <0.1300002502.282120004-1463792638-1022176199 at topica.com> <0.1300002502.282120004-1463792638-1022176199 at topica.com> <0.1300002502.226570442-1463792638-1022418561 at topica.com> <0.1300002502.264636061-1463792126-1022422854 at topica.com>
Content-Type: text/plain; charset=us-ascii
Content-Transfer-Encoding: 7bit
X-RCPT-TO: <michael.welch at homepower.com>
Status: U
X-UIDL: 301093170

Experience counts. Last year Japanese wrenches installed 110 MW of grid-tied PV
including 20,000 approx. 3 kW residential installations. German wrenches
installed 75 MW of grid-tied PV. In just one year they did more than the total
U.S. installed inspected PV systems. Aside from language differences, is there
any reason why there are no German and Japanese wrenches on this list? What can
we do to recruit input from Japanese and German wrenches?

Dana Orzel wrote:

> The dilemma of non wrenches and non wrench salesmen is based on lack of
> installation and material selection experience. Experience teaches lessons.

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================




More information about the RE-Wrenches mailing list