Hi Jay,
At 04:12 PM 5/20/02 -0700, you wrote:
>I sure dont' like to put fuses on the roof. I put my combiner boxes on the
>ground. If there is going to be problem, this is probably the place.
This may depend on the series fuse rating of the particular module used, as
well as the style of junction box.
With Siemens SP 75 modules, with their excellent junction boxes and 15 amp
series fuse rating, I think we can safely use a 15 amp series fuse on each
string, in the j box, without concern.
With a real world charging current of 4.4 amps and a closed circuit
amperage of 4.8 amps, I don't think we would ever blow a fuse unless a
serious fault condition occurred. Even given the multiplier of 1.25 X
1.25, we are still only talking about 7.5 amps. This is 1/2 of the
allowable series fuse rating on an inherently current limited system.
So long as the j box with the fuse is clearly labeled, trouble shooting the
system should not be rendered particularly difficult. Problems that could
blow a fuse would be
1) severely damaged module
2) miswired battery bank with no reverse current protection
3) a condition where a large number of modules were in full sun, forcing
current backward through a miswired module.
4) a ground fault in the series connection between two modules, where open
cable methods were used instead of conduit.
Fuse replacement would seem to me to be a relatively minor issue in any of
these situations.
Does anyone know of any code reason to not put the series fuses in junction
boxes?
Thanks,
Drake
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
</x-flowed>
More information about the RE-Wrenches
mailing list