This is John Wiles' response to questions concerning grounding of a wind
tower as a separate structure.
The preceding thread that led to this is contained in the message below.
Allan @ Positive Energy
----- Original Message -----
From: "John Wiles" <jwiles at nmsu.edu>
To: "Allan Sindelar" <allan at positiveenergysolar.com>
Sent: Monday, April 15, 2002 9:24 AM
Subject: Re: Fw: Lightning Revisited [RE-wrenches]
> Allan:
>
> There are many issues associated with grounding wind turbine systems.
>
> 1. With the exception of the SW Wind Power Air series of wind
> turbines, I know of none that have been through the UL Listing
> process. This process , to a great extent, ensures that the wind
> turbine can be installed in accordance with the requirements of the
> NEC including proper and safe grounding.
>
> 2. There are three-phase delta-connected power systems that have no
> grounded conductor. They still require all metal surfaces (that
> might be energized) to be grounded with equipment-grounding
> conductors.
>
> 3. The best that I can see with the Bergy product is to follow the
> manufacturers instructions. These are based on Bergy's experience
> and should not overtly conflict with NEC requirements.
>
> 4. See 250.4 (B) for grounding ungrounded systems. See 250.24 (D)
> for more grounding requirements for ungrounded ac systems. Section
> 250.32 (A) and (C) give the requirements for grounding two structures
> supplied by a common service (the wind turbine). These (and other
> NEC) requirements need to be addressed in a manner that takes into
> account the location of the rectifier unit. If on the base of the
> tower, then one set of rules would be applied. If located remotely
> from the tower, another set may apply.
>
> 5. With respect to surge (lightning) suppression, what the PV
> industry (including me) does not know would fill many, many volumes.
> I prefer to meet code requirements for grounding and then let the
> lightning and surge control experts take over. The two systems
> (power and lightning protection) are generally separated except when
> they are in contact (wind towers) and then the NEC has some guidance
> in Section 250.106. Surge arrestors are covered in NEC Article 280.
> They type and location of any surge arrestors is best left up to the
> manufacturer of the wind turbine and the manufacturer of the surge
> arrestor. Typically in a three-phase ungrounded delta power system,
> surge protection would be applied phase-to-phase and phase-to-ground.
> Depending on what needs surge protection, surge supression devices
> may need to be applied in more than one location.
>
> 6. As far as I can tell, the wind turbine power lines appear to best
> be converted (rectified) to a grounded dc power signal at a
> disconnect at or before the point of entry of the building. A
> disconnect immediately inside the building at the point of entry
> would also suffice. This would comply with the service entrance
> requirements and the grounding requirements.
>
>
> >----- Original Message -----
> >From: "Allan Sindelar" <allan at positiveenergysolar.com>
> >To: <RE-wrenches at topica.com>
> >Sent: Saturday, April 13, 2002 8:01 PM
> >Subject: Re: Lightning Revisited [RE-wrenches]
> >
> >
> >> Bill, what you describe is what I would do, and fits as a common-sense
> >> approach. We do relatively little wind, as our solar resource is so
> >> reliable, so my opinion isn't based on extensive experience. I'll
forward
> >> this to J. Wiles and post his response.
> >> Allan
> >>
> >> ----- Original Message -----
> >> From: "Bill Brooks" <billbrooks7 at earthlink.net>
> >>
> >> > In the three-phase AC windturbine example there is no grounded
> >conductor.
> >> > All three current-carrying conductors need surge arrestors (probably
> >best
> >> to
> >> > mount the surge arrestors both at the tower, grounded to the tower
> >ground,
> >> > and again at the inverter/controller, grounded to the service
entrance
> >> > ground). I would discuss this with the inspector, but it seems like
> >having
> >> a
> >> > separate tower ground would be okay as long as it sufficient
distance
> >> > (including guy wires) from the building it is serving. Would you
agree
> >> with
> >> > that approach?
> >> >
> >> > Bill.
> >> >
> >> >
> >> > -----Original Message-----
> >> > From: Allan Sindelar [mailto:allan at positiveenergysolar.com]
> >> > Bill,
> >> > I see a possible problem with your recommended solution. The
separate
> >> > structures provision also requires a separate single-point bond in
each
> > > > "structure" between grounding conductor and a grounded conductor.
On the
> >> > three-phase wild AC of many wind generators, what would be the
grounded
> >> > conductor (the equivalent of AC neutral or DC negative)? Have I
missed
> >> > something here?
> >> > Allan at Positive NRG
> >> >
> >> > ----- Original Message -----
> >> > From: "Bill Brooks" <billbrooks7 at earthlink.net>
> >> >
> >> > > What about employing the grounding of separate structures
provision in
> >> NEC
> >> > > 250-32 (2002 code)? If there is a grounded conductor, then that
> >> conductor
> >> > > should be grounded at the tower (or PV Array for PV) and at the
> >service
> >> > > entrance with no ground wire between them and no metalic conduit.
All
> >> > > ungrounded conductors must have surge protection (Phasor, Delta,
> >> voodoo).
> >> > > The main issue is that you cannot touch the tower or module frames
> >while
> >> > > touch something connected to the house. The inverter, however, is
> >> working
> >> > > with conductors that are all referenced to the same grounding
system.
> >>
> >> - - - -
> >> To send a message: RE-wrenches at topica.com
> >>
> >> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
> >>
> >> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
> >>
> >> Check out participant bios: www.mrsharkey.com/wrenches/index.html
> >>
> >> Hosted by Home Power magazine
> >>
> >> Moderator: michael.welch at homepower.com
> >>
> >>
>
>
> --
>
> If I can provide further information, please do not hesitate to call,
> e-mail or fax me.
>
> John
>
> John C. Wiles, Program Manager
> Southwest Technology Development Institute, New Mexico State University
> 505-646-6105 505-646-3841 (FAX) http://www.NMSU.Edu/~tdi/pv.htm
> SWTDI/NMSU
> 1505 Payne Street-Campus
> Box 30001/MSC 3 SOLAR
> Las Cruces, NM 88003
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-Wrenches
mailing list