MPPT arrays in different directions [RE-wrenches]
Gary Higbee, Solutions from the Land
ghigbee at efn.org
Tue Mar 19 17:30:25 EST 2002
Hi Wrenches,
I'd appreciate your thoughts on a large install I'm working on. We've got
about 5kW of PV, though it is divided into South, East, and West fixed roof
arrays. Not optimum, but the architect got to my client before we did.
We're setting up a 48-volt grid-tied system with battery backup. The only
viable inverter solutions I'm aware of for almost immediate delivery are the
Vanner RE48-4500 and the AEI MM-5000. I love the way the MM-5000 is packaged
(built-in 5kW MMPT, ground fault, etc.) but I am concerned about using one
MPPT unit on three different PV orientations. I think I heard that each
different orientation should have its own MPPT controller. Is this true?
If I use the Vanner I'll need 5 combiner boxes, 5 Solar Boost 3048 units,
and all the ground fault and main breakers (the 5 units encompassing 3
directions and current limitations). I'd likely use two Outback DC boxes and
mount the PV controllers in a row above a raceway. I think this could be
done in a clean manner, but the AEI is sure attractive.
So, what do you think--lump the whole roof (East, South, West) into one
giant array with one MPPT and go with the AEI, or break down the roof and
MPPT each direction, using the Vanner/Outback solution?
THANK YOU!
Gary
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Gary Higbee (ghigbee at efn.org)
(541)607-1818 (Eugene)
(541)902-8544 (Florence)
Solar, wind, and hydro site analysis and system design
Components dealer and installation assistance
~Solutions from the Land~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9