The easiest way I've found to deal with this issue is simple.  First section
in the NEC.  Right up front, in plain English.

As Bill Brooks has already stated, a "hold-down" is necessary in a battery
backup situation.

In a purely grid-tied installation, however, the AC circuit is purely an
Individual Branch Circuit per NEC 100.  (As with all code books, it is
listed as "Branch Circuit, Individual".)  I have demonstrated the "drop-out"
to a number of inspectors in the field and reassured them that there are no
"back-up" provisions.

I did have one sharp inspector question "What's the load, if it's a branch
circuit?".  My response to him was, "When the sun goes down, the inverter is
the load".  He's satisfied.  (I know, John B, not much of a load)

To date (over 100 such installs) the Branch Circuit answer has resolved it
every time.

Pray for Sunshine,

Matt Lafferty

PS - If the panel is that old, an upgrade would be appropriate!

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================




More information about the RE-Wrenches mailing list