grounding array/sunny boy [RE-wrenches]

Kent Sheldon kentsheldon at sbcglobal.net
Sat Jan 12 18:20:13 EST 2002


Jay, the Sunny Boy 2500U does ground the PV negative and it has three AC
connections: L1, L2 and PE. The PE connection is not common to either L1
or L2. And it is not inherently common with the AC building neutral.
However, it will appear to be common to the AC neutral through the
system chassis grounds, a ground conductor connected to PE, or any other
paths to earth/neutral ground. If you isolate the SB2500 from the ground
grid (remove all AC and DC connections), you will find that L1 and L2
are not common to PE or the chassis.

The PV negative is grounded inside the inverter through a 1A fuse. This
is consistent with the requirements of NEC 690. You cannot ground the
array anywhere else, or you will create a ground fault, causing the fuse
to clear and the inverter to stop functioning until the other ground is
removed and the fuse is replaced. So you only need to connect PV + and -
to the inverter. The inverter will ground the array per NEC 690.

Let me know if you have any further questions, regards.
____________________________________________
Kent Sheldon
Manager, Industrial Power Systems
SMA America
925 513 8813 Brentwood Office (Primary)
530 273 4848 Grass Valley Office

-----Original Message-----
From: jay peltz [mailto:jay at asis.com] 
Sent: Saturday, January 12, 2002 2:11 PM
To: RE-wrenches at topica.com
Subject: grounding array/sunny boy [RE-wrenches]

Hi John,

Question about grounding array neg on the sunnyboy.  Code says that is
must
be done.

In testing the unit at Schott, it appears that the neg PV is common with
AC
neutral.  If this how its done?

Thanks,

jay

peltz power

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================





More information about the RE-Wrenches mailing list