Todd:
8 circuit load centers cost no more than $45, so the savings is not that
great.
I don't like mixing uses in one load center. I like the client to be
comfortable with their knowledge of the system and I think it would confuse
the client for them to have to understand that every third breaker is the
inverter output. The installation is much cleaner and more logical with
separate load centers for utility, inverter output and another one for
generator.
On the rare occasion I install only one SW inverter, I like to leave an
open space for a second SW inverter. The addition of a second SW inverter
would total mess you up because now you don't have the fourth buss you need.
And not least of all, I'm not sure it would be code legal to mix these uses
in one panel. I didn't bother to look this up because it is undesirable
for the other reasons mentioned.
I too had thought of this idea and immediately rejected it. Hope these
ideas make sense.
William
At 06:43 PM 12/8/01 -0800, you wrote:
>SO... when using a 120 volt only inverter with new construction, I have
>pondered the use of a 3 phase panel. Two of the poles could be for the
>usual split phase 120/240 grid feed. The third pole could be used for
>the 120 volt inverter feed. Neutrals and grounds all bonded in the same
>place, and it has 2 major advantages. One is that it simply looks neater
>having only one panel. The other nice thing is only ONE service
>disconnect for the building. California requires external disconnects
>for power, so this usually means labeling both building panels as
>service disconnects "1 of 2" and "2 of 2" respectively.
>
__________________________________________________________________
William Miller
SLO Communications: Communications and Power Systems Consulting
PO Box 50, Santa Margarita, CA 93453
Voice :805-438-5600 Fax: 805-438-4607 VMail: 805-546-4875
email: wrmiller at slonet.org
License No. C-10-773985
_____________________________________________________________
Compatibility:
Word processor: WP7
Spreadsheet: Quatro Pro 7
CAD: Microstation 95, DXF, Visio 4.1T
_____________________________________________________________
"I stand by all the misstatements that I've made." Dan Quayle
__________________________________________________________________
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-Wrenches
mailing list