Wally:
It sounded to me like your short circuit tests were the only tests with
consistent results for all panels. Is this indeed the case? During short
circuit testing the panels need to be disconnected from all wiring, and
since it appeared your short circuit results were consistent, this tells me
that something external is possibly the problem cause, or is causing the
problem to manifest.
The module voltage under load depends on the load. If the load impedance
is lower, the panel voltage will be lower. If the charge controller is
"pulsing" power into the batteries because of a defect in the controller,
then the panel voltage will fluctuate. If these fluctuations are long in
duration, you may not notice them for the brief time your leads are on a
specific panel. By the time you move to another panel, the situation may
have changed, the charge controller may be drawing more or less current
with corresponding changes in panel loaded volts. This is a long shot, but
it would fit the scenario.
If this job happens to be near my travels, I'd be happy to stop by. I'm in
South County tomorrow (Friday) and North County Monday.
William
At 09:46 PM 10/11/01 -0700, you wrote:
>
>Possibly, if the batteries were almost full. Which they were not.
>But the symptom that concerns me is the low voltage at the modules
>individually.
>>
>OK, but shouldn't the output under load be 16.+ volts and 19 - 21 volts
>open circut?
>Thanks for the suggestions,
>
>Wally
>
__________________________________________________________________
William Miller
SLO Communications: Communications and Power Systems Consulting
PO Box 50, Santa Margarita, CA 93453
Voice :805-438-5600 Fax: 805-438-4607 VMail: 805-546-4875
email: wrmiller at slonet.org
License No. C-10-773985
_____________________________________________________________
Compatibility:
Word processor: WP7
Spreadsheet: Quatro Pro 7
CAD: Microstation 95, DXF, Visio 4.1T
_____________________________________________________________
"I stand by all the misstatements that I've made." Dan Quayle
__________________________________________________________________
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-Wrenches
mailing list