Long delay on response for this one...hope this helps.

If you use the SWCA attached to a computer, it will act just like the SWRC.
You can run those up to 400 feet without changing the size of the cable. 

You can also use the TM500 up to 1000 Feet if you change the size of the
conductor. 

250 feet - 16awg
400 feet - 14awg
620 feet - 12awg
1000 feet - 10awg


Pagan

> -----Original Message-----
> From:	dmccorkl at sover.net [SMTP:dmccorkl at sover.net]
> Sent:	Thursday, August 30, 2001 3:44 AM
> To:	RE-wrenches at topica.com
> Subject:	Long-distance monitor/control of 4024 [RE-wrenches]
> 
> We have a question for the expertise of the group:
> We have an off-grid system, with the house about 175 foot wire run from
> the
> power building.  The customer would like a Remote Control for the SW4024,
> and a meter (we were going to use a TriMetric 2020) in the house.  Trace
> says that's too long for the normal cable for the remote (we were going to
> bury a cable and solder the connectors on each end), and the TriMetric
> didn't work hooked up using wires in a 6-pair telephone direct burial
> cable
> which is already buried.  For the Trace remote, we have heard a little
> about
> converting to serial, then using "short-haul modems", and reconverting,
> but
> don't know the details as yet.  Has anyone had any luck with using a
> longer
> cable for the Trace, and/or has anyone come up with a working solution for
> this kind of distance for either the remote or the TriMetric?
> As usual, thanks in advance for any help with this.
> Doug McCorkle
> SunnySide Solar
> Guilford, VT
> 
> - - - -
> To send a message: RE-wrenches at topica.com
> 
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
> 
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
> 
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
> 
> Hosted by Home Power magazine
> 
> Moderator: michael.welch at homepower.com
> 
> 
> 

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================




More information about the RE-Wrenches mailing list