Windy/Ray, Steve Higgins at Xantrex Arlington caught our thread. This is
apparently a known issue on the SW4048(? on the exact model) when they
experience a voltage surge, especially with lightning and questionable
grounding. Some diodes on the front end of the voltage regulation circuit
can fail and cause the system to regulate around 150Vrms. Knowing that the
scope and the true rms meters are reading this value, it sounds like this
unit needs to be R&R'd before any damage occurs to any of the loads. Please
contact Steve or Dean in Arlington for further clarification. 360-435-8826
#2226 Steve, 360-435-8826 #2220 Dean.

Regards

Kent Sheldon
Sales and Marketing Manager
Distributed Industrial & Utilities Markets
Xantrex Technology Inc.
Direct 925 245 5463 - Fax 925 245 1022
kent.sheldon at xantrex.com  www.xantrex.com


-----Original Message-----
From: Windy Dankoff, Dankoff Solar [mailto:windy at dankoffsolar.com]
Sent: Tuesday, September 04, 2001 9:14 AM
To: RE-wrenches at topica.com
Subject: RE: Overvoltage problem on Trace SW after lightning
[RE-wrenches]


>Does the o-scope read the 152Vrms/210Vp or the meter?

Both

>  Is the meter a true
>RMS meter?

Yes

>This sounds suspiciously like a ground reference/measurement
>problem.

Checked!!

>  You did mention there may be problems with the ground grid at this
>site.

Just mediocre earth contact because of dry earth. But, everything done
right.

Ray Walters will take it from here. He's the installer.

  ... Hey, Ray??


Windy

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================






More information about the RE-Wrenches mailing list