Grid Tie 240 VAC w/ transfer switch? [RE-wrenches]

Allan Sindelar allan at positiveenergysolar.com
Wed Aug 8 21:38:59 EDT 2001


Chris,
I researched the same thing, but never ended up doing it. We have used
ASCO's transfer switches several times in generator backup situations with
Kohler generators. It should work. By the way, you might look into Kohlers
G120 line (homeowner grade, no bells or whistles) of 100A and 200A ATSs as
well, to save $$$.

You will need a small panel ahead of the main load center, but after the
meter, from which to feed 2P 60A to AC1. As an alternative, you could use a
2P AC contactor energized by grid AC to shut off AC from the main load
center to AC1. And I suspect there are other approaches that would work too.

Allan at Positive Energy

----- Original Message -----
From: Chris Daum <info at oasismontana.com>
> My client's system is in California; he has two Bergey XL 1's on order,
and
> has two Trace SW4024's and six 120W modules.  He is in a place with
rolling
> power outages and wants back-up (vis a vis eight of the Surrette S460
> batteries).  His power is rarely out for more than an hour at a time.  His
> site offers excellent sun and winds, with 15 to 18 mph averages.
>
> But, he doesn't want a separate sub-panel for his important loads.  Has
> anyone done a grid-tie with a transfer switch (located before the main
> electrical service panel), where one side of the transfer switch is from
> utility power, and the other leg is 240VAC from the inverter's output?  My
> client wants total back up not just dedicated loads, and says he'll "power
> down" in the event of a power failure (and yes, I've cautioned him that if
> the grid fails, it would be easy to max out his inverters). There is no
> fuel generator integrated into this system.
>
> I've talked with a nice fellow from Asco (http://www.asco.com) about
> whether their transfer switches would work for this application.  We both
> think it would--but know of no one who's tested or tried this.
>
> One thing I'm uncertain about, code-wise, is feeding the utility input
into
> the AC 1 "in", from the utility side of the transfer switch (like, with a
> separate 60A circuit breaker).

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!