grounds [RE-wrenches]

Drake Chamberlin - Electrical Energy solar at eagle-access.net
Sat Aug 4 13:33:00 EDT 2001


<x-flowed>
Foundation grounds, water pipe grounds and ground rods are supposed to be 
bonded together at the neutral in the enclosure with the service 
disconnect.  The neutral bus at the service disconnect is the only place on 
a premise where the grounded current carrying conductor is permitted to be 
grounded.

In another building fed by the same service, it is permitted (and often 
required) to bond the neutral to another ground rod and any other grounding 
electrodes that are available.

Drake

At 09:22 AM 08/04/2001 -0700, you wrote:
>How does this apply to foundation (u-fa) grounds?
>
>Todd
>
>Drake Chamberlin - Electrical Energy wrote:
>
> > My recollection of the code on this is that of two rods are within six feet
> > of each other, they should be bonded together.
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================




</x-flowed>


More information about the RE-Wrenches mailing list