SW 5548 [RE-wrenches]
Drake Chamberlin - Electrical Energy
solar at eagle-access.net
Sat Jun 16 13:06:12 EDT 2001
<x-flowed>
Induced voltage is very common in wiring in general. I find it regularly
when troubleshooting. It is especially common in switch legs, where an
open wire runs next to a wire with ac voltage. Although it is annoying, it
isn't hazardous. Sometime the induced voltage is sufficient to light an
induction type voltage probe, which does produce false readings. A multi
meter is necessary to diagnose wiring where this induced voltage is present.
Drake
At 12:01 PM 06/14/2001 -0400, you wrote:
>Not related to a Trace installation, but in doing some house wiring I've
>found 24V induced currents in wires. (Both ends of the wire (romex 12/2
>w/G) disconnected, measured voltage on both ends. As I pulled the wire from
>the wall to prove to myself that it was induced voltage, the voltage slowly
>dropped off, until, you guessed it, lying on the floor in a pile there was
>no voltage.)
>
>Clearly this voltage had no amperage behind it, unless the cable it was
>next too had a tremendous voltage. (which it did not, being house wiring).
>Placing the wires in separate conduits (one for each + - pair) would solve
>the "problem". Understanding it solved it fro me, and the cable went back
>into place.
>
>Jeff
>
>Jeffery D. Wolfe, P.E.
>Global Resource Options, LLP
>A Woman-Owned Limited Liability Partnership
>4 Kibling Hill Road
>P.O. Box 51
>Strafford, VT 05072
>800-374-4494 Toll Free
>802-765-4632 Phone
>802-765-9983 Fax
>global at sover.net
>http://www.GlobalResourceOptions.com
>
>----------
>From: Jerry Caldwell[SMTP:solarcowboy at yahoo.com]
>Reply To: RE-wrenches at topica.com
>Sent: Tuesday, June 12, 2001 1:23 AM
>To: RE-wrenches at topica.com
>Subject: SW 5548 [RE-wrenches]
>
>About a week ago a local inspector gave me a hard time
>over a recent installation. He asked me to
>demonstrate to him that the SW5548 inverter could
>power the backed up subpanel while not sending any
>voltage to the grid. I set the inverter to float mode
>and showed him 120v at the subpanel. When I went to
>the ac disconnect, which was in the open position, my
>meter showed ~24v ac hot to ground on the inverter
>side of the switch.
>
>I asked one of the tech support guys at Trace about
>this and he said it was "noise" and that there was no
>power behind the voltage.
>
>Can anyone contribute a little more to this so I might
>be able to better explain this in the future?
>
>Jerry Caldwell
>Light Energy Systems
>
>__________________________________________________
>Do You Yahoo!?
>Get personalized email addresses from Yahoo! Mail - only $35
>a year! http://personal.mail.yahoo.com/
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
</x-flowed>
More information about the RE-Wrenches
mailing list