Solar Boost / C40 test/ Allan Qs [RE-wrenches]

blair Tump may tump at midcoast.com
Sat May 5 08:27:50 EDT 2001


<x-flowed>
Allan, Check the Temps again, as far as the voltage drop from combiner box 
to CC input:.014 Vts.  The MPPT I usually do tweak a bit but Rick sends the 
units out pre set for the BP 585 current output so between us both I'm sure 
its close.



>     A PV input voltage of 28.5 is low enough to suggest that one or more of
>these may apply:
>* An extremely hot day and module temperature
>* Excessive input voltage drop
>* MPPT adjustment on the SB50 not set optimally.
>I would expect to see an input voltage of around 35 volts before temperature
>deration. Any ideas?
>Allan at Pos Energy
Solarwinds NorthernLights
Serving Mid Coast Maine & Northern California
          610-517-8401              707-498-2804









- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A  -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
==^================================================================

</x-flowed>


More information about the RE-Wrenches mailing list