Trace TM500 [RE-wrenches]

Chuck Heath, SunPower sunpwr at jps.net
Tue Apr 10 19:55:47 EDT 2001


William Miller asked:
> Has anyone on this list researched
>how far one can locate a TM 500 from the shunt and batteries?

I have one where the meter and shunt are 350 ft. apart. I cut the TR500 
cable at a junction box about 15 ft. from the shunt, installed a 
screw-type terminal strip, and made the long run using #16 AWG (signal) 
and #14 AWG (power) to another junction box at the house end, and 
connected to the other end of the TR cable. Works fine.

Since the TR cable wire is so small, I stripped double the normal length 
to fold-back each wire, doubling the thickness of the wire entering the 
term strip.

Installation note: be careful of the shunt orientation. Otherwise you may 
have difficulty getting past the 4/0 cables to plug in the RJ-11 cable.

I've done the same with the TriMetric (which licensed their circuitry to 
Trace) over distances of 400+ feet. No problems.

Cordially, Chuck 

- - -
To send a message:
 RE-wrenches at topica.com

Archive of previous messages: 
 http://www.topica.com/lists/RE-wrenches/

List rules & etiquette:
 http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator:
 michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A  -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
==^================================================================



More information about the RE-Wrenches mailing list