Rob,
Thanks for the great specific information.
Bill.
-----Original Message-----
From: Rob Wills [mailto:RWills at AdvancedEnergy.com]
Sent: Wednesday, March 28, 2001 9:06 AM
To: RE-wrenches at topica.com
Subject: RE: Combiner box alternate solutions [RE-wrenches]
My Buss catalog shows type ABC to be DC rated as follows:
UL listed 0-15A
UL recognized 20-25A
DC rating is 250V up to 20A and then 125V.
DC ratings are "self certified" which should be fine for the inspectors.
==================================================
The Littlefuse 3AB is DC rated as follows:
UL listed 0-15A
UL recognized 20-30A (note the difference - if you need a 30A fuse, it must
be Littlefuse)
DC rating is 250V up to 20A and then 125V.
No mention of self certification
==================================================
Bill's comment about listed and recognized is important to understand:
Listing is for complete pieces of equipment
Recognition is for components intended to be used in (typically listed)
equipment
Regards
Rob Wills
Advanced Energy
PS We are evaluating the cost trade-offs of making string combiners with
PCBs Vs. DIN rail fuse holders and blocks in high volume manufacturing -
I'll keep you informed as to how it comes out..
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
List rules & etiquette:
http://www.mrsharkey.com/wrenches/etiquete.htm
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
____________________________________________________________
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
List rules & etiquette:
http://www.mrsharkey.com/wrenches/etiquete.htm
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
==^================================================================
More information about the RE-Wrenches
mailing list