Bill Brooks wrote:
> 
 The Heinemann
> is rated for 10,000 AIR which is questionable for paralleled battery banks.
> 

My specs for the Heinemann GJ shows 25,000 AIC at 65VDC.  The 10k number
is at 125VDC.  There's a pretty good article in HP 27 called Overcurrent
Protection for Battery Powered Systems.  It measured 6960 max amps thru
a dead short from 4 used 6 volt golf cart batteries wired at 12 volts.

Jack West

- - - - - - -