Just in from Square D [RE-wrenches]

Bill Brooks billbrooks7 at earthlink.net
Mon Mar 12 00:52:19 EST 2001


Signal circuits below 50 volts do not fall under the NEC. All power handling
circuits, regardless of voltage must follow the code. Signal circuits above
50 volts (e.g. 120Vac thermostat circuits) do fall under the NEC.

My understanding from these emails is that this is dealing with a signal
circuit. As long as the wire is protected by a properly sized fuse, pick any
wire size you like. No Fascism necessary.

Bill.

-----Original Message-----
From: Allan Sindelar, Positive Energy, Inc.
[mailto:allan at positivenergy.com]
Sent: Saturday, March 10, 2001 5:30 PM
To: RE-wrenches at topica.com
Subject: Re: Just in from Square D [RE-wrenches]


----- Original Message -----
From: "hugh piggott" <hugh.piggott at enterprise.net>
Conductors shall not be smaller than No. 12 copper or equivalent.
>
> that's a bit fascist.  What about circuits with 1 amp fuses?

Yeah, I am wondering about this, too... We do signal circuits with float
switches running coil circuits (all 170 mA or less) of DC-coil relays with
18 AWG float switch cable, and LED lights (in multiples of 25 mA), for
example.  Are these considered "circuits"? Bill Brooks (or any wrench), what
is the intent of the code here, and can circuits of this nature (often with
additional AGC or ABC in-line supplemental fusing) be exempted via other
code sections?

Good $5 (3 pound?) word, Hugh, "fascist".

Allan @+E

- - - - - - -
To send a message:
 RE-wrenches at topica.com

The archive of previous messages:
 http://www.topica.com/lists/RE-wrenches/

List rules & etiquette:
 http://www.mrsharkey.com/wrenches/etiquete.htm

To unsubscribe send a message to:
 RE-wrenches-unsubscribe at topica.com

To check out the other RE-Wrench participants:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine:
 www.homepower.com

For info contact list moderator by email:
 michael.welch at homepower.com

____________________________________________________________
T O P I C A  -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01

- - - - - - -
To send a message:
 RE-wrenches at topica.com

The archive of previous messages: 
 http://www.topica.com/lists/RE-wrenches/

List rules & etiquette:
 http://www.mrsharkey.com/wrenches/etiquete.htm

To unsubscribe send a message to: 
 RE-wrenches-unsubscribe at topica.com

To check out the other RE-Wrench participants:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine: 
 www.homepower.com

For info contact list moderator by email:
 michael.welch at homepower.com

____________________________________________________________
T O P I C A  -- Learn More. Surf Less. 
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01



More information about the RE-Wrenches mailing list