Just in from Square D [RE-wrenches]

Allan Sindelar, Positive Energy, Inc. allan at positivenergy.com
Sat Mar 10 20:12:59 EST 2001


If I cogitate (that's one a them five-dollar words like "paucity") on this,
it appears that we can't take advantage of the option of using 2-pole QO
breakers and load centers to allow higher-voltage DC operation, because of
the fundamental NEC requirement that one conductor (in our case the DC
negative) remain grounded. Unless I'm missing something, the circumstances
under which the 125 VDC rating is achieved don't work in the standard
"bond-the-negative-at-one-point-and-break-the-positive" approach that has
become the NEC-compliant standard, so the issue is moot.

I have never heard anything to suggest that breakers could not be sized
below conductor ampacity for DC. If it's true, we're in big trouble, because
sizing for voltage drop nearly always upsizes wire relative to sizing for
ampacity.

Can anyone elucidate (whups, jest slipped out)?

Allan @ Pos E
> Yup, I will admit that I am not well versed in this area of the code,
> but I do remember that at specific voltages, (low Voltage) DC systems
> could go ungrounded, but you had to provide current interrupt/disconnect
> (or was it current limiting?) on both the Pos and Neg.  Wonder if it
> would meet code to use a standard QO box, and bring the Pos in on one
> breaker leg and the Neg. in on the other breaker buss, then just use two
> poles?

> I once had a Square D guy tell me that a 15 amp QO breaker sould NOT be
> used on a circuit supplied with a 12 gauge wire.  He said it was just as
> bad as using a 20 amp breaker on a circuit supplied by a 14 gauge
> wire.   The large conductor changes a bunch of stuff that makes the
> breaker break when it should?   We're often lowing resistance as far as
> possible.  Cool?


- - - - - - -
To send a message:
 RE-wrenches at topica.com

The archive of previous messages: 
 http://www.topica.com/lists/RE-wrenches/

List rules & etiquette:
 http://www.mrsharkey.com/wrenches/etiquete.htm

To unsubscribe send a message to: 
 RE-wrenches-unsubscribe at topica.com

To check out the other RE-Wrench participants:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine: 
 www.homepower.com

For info contact list moderator by email:
 michael.welch at homepower.com

____________________________________________________________
T O P I C A  -- Learn More. Surf Less. 
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01



More information about the RE-Wrenches mailing list