Battery sizing for running the SW [RE-wrenches]
sunwise at cheqnet.net
sunwise at cheqnet.net
Sat Feb 24 18:09:58 EST 2001
> > if maintaining a stable float seems to be a problem at night, maybe it
> > would help to turn the AC1 charging amps way down
>
Doug Pratt wrote:
> That helps, so does turning the absorption volts way down, the float volts
> down, adjusting the float time to minimum, etc., etc. There's lots of
> tinkering you can do to minimize charging wattage,
Hey Doug,
I agree, but actually I wasn't speaking to the issue of attempting to
improve grid-tie efficiency by turning down the charger amps (a whole
nother issue with its own can of worms). I was saying that if you do
put an extremely small battery (200AH) on an SW and leave the charging
amps at the 30A default, the resulting C/6.6 charge rate could have
problems associated with it that go beyond efficiency. -- Kurt Nelson
- - - - - - -