I bet if you watch the generator voltage under load it is dropping under the
inverter lower limit and shutting the charger down.
I have seen this on SW's but they have adjustable limits, I don't think the
1524 is adjustable (lousy memory).
You need a higher voltage from the generator or a 10% boosting transformer
would help. I think Kurt has them.

Later,
Bob

-----Original Message-----
From:	Lee Tavenner, Solar Plexus [mailto:solplex at montana.com]
Sent:	Tuesday, February 13, 2001 2:09 PM
To:	RE-wrenches at topica.com
Subject:	inverter generator match [RE-wrenches]

Wrenches:
I have a customer with a Trace 1524 inverter and a Kawasaki 3200 watt
generator.  When the generator starts up, the Trace inverter after  60
seconds will go into bulk charge only for a second, then it will revert
to inverter mode.  The battery voltage is about 24.5 volts, the
frequency is slightly high, about 62 hz, but according to Trace not out
of range, and the generator voltage is about 112 volts.  The inverter
charges properly on the grid and it charges properly with a different
generator.  Is there something peculiar about the Kawasaki  generators
that could cause such a problem?  Has anyone else had similar
experience?  What is going on here?  Thanks.  Lee Tavenner. Solar Plexus

- - - - - - -
To send a message:
 RE-wrenches at topica.com

The archive of previous messages:
 http://www.topica.com/lists/RE-wrenches/

To unsubscribe send a message to:
 RE-wrenches-unsubscribe at topica.com

To check out the other RE-Wrench participants:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine:
 www.homepower.com

For info contact list moderator by email:
 michael.welch at homepower.com

____________________________________________________________
T O P I C A  -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01


- - - - - - -
To send a message:
 RE-wrenches at topica.com

The archive of previous messages: 
 http://www.topica.com/lists/RE-wrenches/

To unsubscribe send a message to: 
 RE-wrenches-unsubscribe at topica.com

To check out the other RE-Wrench participants:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine: 
 www.homepower.com

For info contact list moderator by email:
 michael.welch at homepower.com

____________________________________________________________
T O P I C A  -- Learn More. Surf Less. 
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01



More information about the RE-Wrenches mailing list