series circuits for Sunny Boy [RE-wrenches]
Travis Creswell, Ozark Solar
ozsolar at ipa.net
Mon Dec 3 08:18:33 EST 2001
Thanks for pointing that out Jeff. I have used a truckload of them for 480
vac applications but never for DC applications over 48 vdc. Hopefully, I
would have studied that a little closer before I did a battery less system.
That's the great thing about this list.
I would still like to be able to use a handle to disconnect a system rather
than have to use tools to open a box (wasp home) and carefully remove a fuse
(buried under that wasp nest).
Travis
----------
>From: "Jeffrey Wolfe, Global Resources" <global at sover.net>
>To: "'RE-wrenches at topica.com'" <RE-wrenches at topica.com>
>Subject: RE: series circuits for Sunny Boy [RE-wrenches]
>Date: Sun, Dec 2, 2001, 11:48 PM
>
>Travis,
>
>One fine print note on using some of the SqD disconnects. The 600VDC
>rating on some of them depends upon breaking BOTH the hot and the negative,
>using the outside poles of a three phase unit. The only unit I see in my
>Grainger book that avoids this requirement is the 200A 4-wire switch, (but
>it's not really clear it's listed for DC, and the Square D catalog does not
>rate it for DC>)
>
>So you're into either multiple switches or ignoring the rating. The rating
>is *probably* made in consideration of breaking the DC under load at a
>level of 200A, but still and all, that's the rating.
>
>I'd stick with the combiner box.
>
>Jeff
>
>On Sunday, December 02, 2001 6:53 PM, Travis Creswell, Ozark Solar
>[SMTP:ozsolar at ipa.net] wrote:
>> Check out page 458 of the Grainger No. 392 catalog. You'll have to buy a
>3
>> phase model and that will give you 3 sub arrays. You can get a Nema 3R
>> Rainproof ST/3P 600 VDC fusible disconnect (30 amp, Square D flavor) for
>> $401.75.
>>
>> Does the Trace Tech model have a handle or do you have to open the box
>and
>> remove the fuses.
>>
>> And be ever so careful about trying to "educate inspectors". Do want he
>> wants on this job with a big smile on your face then carefully challenge
>him
>> next time. Tell him how smart he is and thank him (for making life
>> difficult) and your life will be so much easier next time. They are the
>> final authority so if they feel like it they can make your life very
>> difficult.
>>
>> Travis Creswell
>> Ozark Solar
>> ----------
>> From: "Mangelsdorf, Marco" <mmangelsdorf at hei.com>
>> To: RE-wrenches at topica.com
>> Subject: series circuits for Sunny Boy [RE-wrenches]
>> Date: Sun, Dec 2, 2001, 5:14 PM
>>
>>
>>
>> Aloha Wrenches,
>>
>> Does anyone know of a relatively low cost high voltage (up to 600 VDC)
>> combiner box that has, say, two or three fuse holders?
>>
>> We've finished the first Sunny Boy 2500U installation here in the islands
>> with two parallel series-wired sets of (10) BP 150-watt 24 VDC modules.
>> According to a reasonable interpretation of the NEC 690-9 (b), there is
>no
>> need for fuse protection of each series circuit of modules. So, in the
>> install, I have both sets of modules wired directly to a single pair of
>> #10CU conductors with no fuses. The inspection did not pass last friday
>> with the notation being that there was no overcurrent protection on the
>> roof, i.e., no combiner box with separate fuses to protect each series
>> string. I'm going to try and educate our local authorities tomorrow on
>the
>> lack of need for fuses on the roof with a cover letter of my own and a
>> two-page letter that John Berdner of SMA-America has been kind enough to
>> supply me with. BUT....in case I don't prevail in my education process,
>I'm
>> looking for a low cost plan B. I know that I can get a 10-circuit
>combiner
>> from Trace Tech. that's rated at the high DC voltage. But I'd like to
>avoid
>> spending $400 or more bucks for it.
>>
>> Any ideas?
>>
>> thanks,
>> marco
>>
>> Marco Mangelsdorf, Ph.D.
>> Marketing and Sales
>> ProVision Technologies, Inc.
>> 69 Railroad Avenue, Suite A-7
>> Hilo, Hawaii 96720 USA
>> (808) 969-3281, fax 934-7462
>> www.provisiontechnologies.com - - - -
>> To send a message: RE-wrenches at topica.com
>>
>> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>> <http://www.topica.com/lists/RE-wrenches/>
>>
>> List rules etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>> <http://www.mrsharkey.com/wrenches/etiquete.htm>
>>
>> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>>
>> Hosted by Home Power magazine
>>
>> Moderator: michael.welch at homepower.com
>>
>> - - - -
>> To send a message: RE-wrenches at topica.com
>>
>> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>>
>> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>>
>> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>>
>> Hosted by Home Power magazine
>>
>> Moderator: michael.welch at homepower.com
>>
>> << File: ATT00001.htm >>
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-Wrenches
mailing list