At 04:34 PM 08/11/2001 -0700, you wrote:
>List members,
>
>Doug Pratt wrote:
>
> > 3. Multiple ground rods in a single system are fine, but they MUST all
> be connected
> > together. If those connections are bare #8 wire in direct contact with
> the ground
> > (not in conduit), then it's even easier for the lightning energy to
> dissipate.
> > So put in a ground rod at your PV array, put in a ground rod at the
> base of your
> > wind tower, AND at each guy wire anchor, but HOOK THEM ALL TOGETHER
> with buried
> > wire!
>
>Sometimes this is not practical when running long 150+' runs in from the
>PV/ wind
>gennys. Are you saying you want 150' of #8 or #4 bare copper in the trench
>with the RE
>delivery wires?
In this situation, the rods do not need to be bonded together in this
way. The locations are separate. In the wiring for buildings, a ground
rod is bonded to the neutral at the disconnect for the separate
structure. A separate conductor connecting the rods would create a
parallel neutral path.
Drake
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
</x-flowed>
More information about the RE-Wrenches
mailing list