grounds [RE-wrenches]

Allan Sindelar, Positive Energy, Inc. allan at positiveenergysolar.com
Mon Aug 6 16:33:19 EDT 2001


Hugh,
In our country, tying a current-carrying conductor to ground at one point is
called bonding. You then have a "grounded" conductor--the neutral, which is
current-carrying but has zero potential to ground--and a "grounding"
conductor (the bare or green), which carries current only in a fault
situation.
It's confusing also because multiple ground rods are "bonded" together, so
there can be no potential between them. Trace emphasizes bonding AC and DC
ground paths together because otherwise that potential (such as a
lightning-induced surge) fries stuff in the inverter, where both come
together.
Does this help?
Allan at Pos Energy

----- Original Message -----
From: hugh piggott <hugh.piggott at enterprise.net>

Current carrying conductors are also 'bonded' to ground, (usually
> at one point only for each supply, so as to prevent the grounding
> system from sharing the power circuit).
>
> Each of these connections is referred to as grounding, and this
> creates great ambiguities.

> I read in the Trace tech note that all equipment should be grounded
> at one point.  I assume this means connecting all ground rods
> together and all equipment together and then making a final single
> connection between the two systems at one point.

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================






More information about the RE-Wrenches mailing list