grounds [RE-wrenches]
Travis Creswell, Ozark Solar
ozsolar at ipa.net
Sun Aug 5 15:53:34 EDT 2001
Don,
Other than lightning protection (and code) do you see a need to ground 12
volt systems with no inverter.
Travis
----- Original Message -----
From: "Don Loweburg, Offline" <i2p at aol.com>
>
> The thing is that NEC really does not address lightning protection. Their
> grounding protocals address safety only. The point that Bob-O makes is
sound,
> but if you don't bond the two grounding systems, you are violating NEC.
>
> This is what I do when faced with the possiblity of lightning (this is non
> compliant). At the array I ground everything very well, and use an
arrestor
> with the ground connected to the local ground system. I don't bond. At the
> other end I again use another arrestor, this time bonding all grounds.
>
> It's not ignorance, rather its a very slippery subject without consensus.
>
> Best, Don
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-Wrenches
mailing list