48V hardware [RE-wrenches]

Allan Sindelar allan at positiveenergysolar.com
Thu Jul 19 17:15:04 EDT 2001


Note that my original request was for sources and solutions to 48V
switchgear for signal sources. Nobody has provided that yet, although I
appreciate the efforts. Del City makes inexpensive SPST and SPDT switches
rated (by them) 24V 50A; these ought to work 48V 1/20th amp. DPDT are 21A,
14V. That's the closest I have found. Anyone else?
Allan
----- Original Message -----
From: Kent Sheldon <kentsheldon at tracetec.com>

> yes and no bill, switches may be operated under the peak ac voltage
> rating (125 x root2), as long as they are not used for load  breaking.
> system isolation purposes only is fine. voltage clearance is not the
> issue, current breaking with no zero crossing is. you are correct about
> the ul rating, the device must be rated for the application to realize
> the listing. and current protection devices must be listed and rated
> for any dc application.
>
> Kent


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================



More information about the RE-Wrenches mailing list