I have been keeping these Onan notes, as two days ago I did a service call
involving the same problem. In this case the Trace started and stopped the
Onan without problem from the menu bar. But the Onan remote in the home
could not also start and stop the unit. As such, I couldn't manually start
the generator with the SW in EQ mode to manually initiate an EQ of the
batteries.
The client is not savvy enough to handle a workaround with the inverter
(it's now a rental home).
Any tips on paralleling Onan's factory remote or on-unit start switch with
the SW? Thank you.
Allan at +E
----- Original Message -----
From: Drake Chamberlin - Electrical Energy <solar at eagle-access.net>
To: <RE-wrenches at topica.com>
Sent: Friday, July 13, 2001 9:40 AM
Subject: Re: Trace/Onan starting [RE-wrenches]
> Hi Dave,
>
> I found my notes from when I talked to Gary at Trace several years back,
> concerning the auto start on the Onan. The manual that I used is for
> Version 4.01.
>
> The manual stated:
>
> "For this type of generator, relay RY 8 duplicates the "START" position
and
> relay RY 7 is used to duplicate the "STOP" position (using the common and
> normally closed contacts). "
>
> Gary at Trace told me that the error in the above quotation from the
manual
> is that both relays must use the common and normally open contacts. The
> generator connected in this way has started (and stopped) reliably from
the
> inverter for several years.
>
> Drake
>
>
> At 03:17 PM 07/12/2001 -0400, you wrote:
> >Wrenches,
> >This just came in today. I did not do the install, or sell the equipment.
> >Any body have any experience with Onan's and Trace SW remote starting?
> >"Dave - In my house I have a Trace SW series
> >inverter/charger. I have two Onan generators, the
> >first, 6.3 NHDFB 7512M, propane fueled, the second, a
> >JC Industrial Engine, 12.5 Kwatt, 1964 vintage,
> >propane fueled, can be converted for gas operation.
> >I had the 6.3 NHD hooked up using a 3 wire start
> >setup. All the electrical work was done by a licensed
> >electrician, who had no previous Onan/Trace
> >experience. When I would start the generator via the
> >Trace unit. The generator would start no problem but
> >as soon as it would start, a grinding noise would
> >occur & the generator would shut down. I put 4
> >starters into this unit. I then purchased the second
> >Onan generator, convinced that the first generator was
> >a lemon. I still have the same 3 wire hook up. Now the
> >second generator is doing the same thing. The last two
> >times that grinding noise has come about, I have
> >immediately shut the generator off via the Trace unit,
> >& walked out to the generator & started the generator
> >via the Start/Stop switch located on the generator. It
> >starts fine with no grinding. I would appreciate any
> >assistance that you might have to offer. Thank you. - Jim______"
> >
> >Dave
> >
> >- - - -
> >To send a message: RE-wrenches at topica.com
> >
> >Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
> >
> >List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
> >
> >Check out participant bios: www.mrsharkey.com/wrenches/index.html
> >
> >Hosted by Home Power magazine
> >
> >Moderator: michael.welch at homepower.com
> >
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-Wrenches
mailing list