Carflex revisited [RE-wrenches]
Travis Creswell, Ozark Solar
ozsolar at ipa.net
Mon May 28 22:42:49 EDT 2001
Hi Bill,
How did the water get in the junction box? I have never seen a water filled
junction box in my 10 years of solar but there is no way I have looked at
anywhere near as many modules as you have. Usually I open them up only to
find those dry little cob webs and some dry dead spider in there.
Another point regarding the 90c rating for wire. You'll find very over
current protection devices rated at any other than 60/75c so you cannot use
the ampacity rating of the wire @ 90c on that over current protection
device. You have to use the rating and 60/75c. Grab any breaker and see
what it says.
Travis Creswell
Ozark Solar
----- Original Message -----
From: "Bill Brooks" <billbrooks7 at earthlink.net>
To: <RE-wrenches at topica.com>
Sent: Monday, May 28, 2001 7:14 PM
Subject: RE: Carflex revisited [RE-wrenches]
> I have opened several module junction boxes that were full of water as
were
> their conduits
> Many
> electricians are often confused when the most common wire we use has the
> ratings THHN(90C Dry) or THWN(75C Wet). Does this mean we get to pick
which
> rating we like best? No it means that when applied in a "Dry Location" as
> specified in Article 100 above, that it carries a 90C rating and when it
is
> applied in a "Wet Location" as specified in Article 100 above, that it
> carries a 75C rating
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-Wrenches
mailing list