PV Module Degradation (was PV Inverters module strings) [RE-wrenches]

Pat Kiernan, Eco Electric, Inc. ecoelec at rof.net
Mon May 14 21:00:16 EDT 2001


Bill Brooks,

I would really like to see the PVUSA documentation you mention if it is
available. The reports I've seen indicate 0.5% power degradation per year
with voltage degradation largely due to increasing resistance in connections
and current degradation due to optical degradation in the
encapsulant/lamination.

If 1-2% module power degradation per year is real than most PV warranties
are a hoax and RE is a little closer to snake oil than I would like.


Pat Kiernan

Eco Electric, Inc.
PO Box 550
Carbondale, CO 81623
tel/fax (970) 963-3132
e-mail: ecoelec at rof.net
----- Original Message -----
From: Bill Brooks <billbrooks7 at earthlink.net>
To: <RE-wrenches at topica.com>
Sent: Thursday, May 10, 2001 1:40 PM
Subject: RE: PV Inverters module strings (Last Call) [RE-wrenches]


> Carl,
>
> No self-respecting PV manufacturer is going to share eventual
> underperformance numbers. They are non-the-less very real and are fairly
> consistent with all PV technologies available. No special conspiracy
theory
> for a-Si. All systems degrade at 1-2% per year and most of the degradation
> seems to occur in voltage. Documented at PVUSA with over 20 systems of all
> types over 10 years.
>
> Initial overperformance is probably only an issue if you start a system
> during the colder time of year. Most inverters, I believe this includes
> Trace Tech (Kent please chime in) will stay offline with a DC overvoltage
> condition should the Voc get over 600 Volts initially. As the array warms
in
> the sun and degrades, that voltage will settle into the proper range and
the
> inverter will start.
>
> Bill.
>


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A  -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
==^================================================================



More information about the RE-Wrenches mailing list