OK you folks heres the raw data, sorry travis that spread sheet stuff
would have taken me till next week!
All measurments were taken w/ a Fluke 87, Fluke clamp on AC 80i 400 / DC
80i1010 amp probes.Watts w/ a Brand Electronics transducer at AC L1to the
grid. DC measured at the Batt cable in DC disconnect box to inverter.Temp
was a fluke thermocoupler K type surface probe.
Site; N44* W 069* temp amb; 92.2* panel top temp;117* back of panel
124.2* array ang;44* facing;185* M Elv;170'
System SW 4024 * 375 surrette batts.15 585 panels & 1 590 panel wired 24vt DC
C40' Battery voltage;25.46 panel voltage 26.32 DC amps in 39.5-40 AC
amps to grid 7.62 Brand WT Mtr 930 Avg
Solar Boost 50; Batt.Vt.25.46 Panel Vt.28.5 DC Amps in 40.9-41.2 AC Amps
into grid 8.1 Brand WT Mtr; 970 Avg
REMEMBER REMOVE THE BONDING SCREW IN DC DOX IF APPLICKABLE ALSO USE DELTA
LIGHTNING ARRESTORS SOLAR BOOST MUST NOT BE GROUNDED BEFORE CHARGE CONTROLLER.
Solarwinds NorthernLights
Serving Mid Coast Maine & Northern California
610-517-8401 707-498-2804
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
==^================================================================
</x-flowed>
More information about the RE-Wrenches
mailing list