Hi Joel,
One way is to increase the number of batteries in the system. This increases the
operating voltage ( more watts) without the need for a MPPT controller. 48v systems
are pretty easy as you add another 6v ( if you are using 6v batteries. If you are
using 2v cells, then maybe 8v would work better?) battery to the system, works
pretty slick- cell voltage is lower, overall voltage is higher= more watts to the
grid.
And yes many people are using the MPPT controllers to get around this problem called
"batteries".
Jay
Peltz Power
Joel Davidson wrote:
> Yes, I have 32 each 70-watt modules 4 in series for nominal 48 volts. The C40 is
> set at 54.8 volts so that voltage flows downhill to the inverter which is set at
> 54.4 volts.
>
> Note that this is a grid tied net metered PV system with batteries - not a stand
> alone or standby PV system.
>
> The problem with a net metered PV system using the SW-series inverter with
> batteries is that the inverter operates at the nominal battery voltage, not the
> optimum PV array max power point. Since the batteries are just sitting there
> being float charged and power passes through the inverter to the load and grid,
> can the SolarBoost send max power from the array to the inverter? Has anyone
> used a SolarBoost to get around this SW inverter shortcoming?
>
> "Travis Creswell, Ozark Solar" wrote:
>
> > Joel,
> >
> > Are you trying to say you have thirty two 70 watt modules? 8 strings x 4.?
> > amps = 30 + amp array. You will need two Solar Boost 3048's. Better yet
> > put 16 on the C40 and 16 on the SB3048 (you'll need a DVM option for it too)
> > and compare the outputs. Do you have a Fluke 36 ammeter? If you don't
> > borrow/buy one (~$250 and you really should have one) and compare it's amp
> > rating to your C40's. I almost always find the C40 DVM's to read amps ~10%
> > low. I have found the SolarBoost products to be very accurate. (Never pass
> > a chance to beat up on Trace, just kidding, maybe)
> >
> > Oh yeah, your question, you should produce up to 30% more amps when its
> > colder, say less than 40F. In the summer you will only see a 10% (maybe)
> > difference when the batteries are under 50 volts in the cooler mornings
> > which you won't see since you are grid tied.
> >
> > Travis Creswell
> > Ozark Solar
> >
> > ----- Original Message -----
> > From: "Joel Davidson" <joeldavidson at earthlink.net>
> > To: <RE-wrenches at topica.com>
> > Sent: Wednesday, May 02, 2001 6:51 PM
> > Subject: Re: Voltage drop musings [RE-wrenches]
> >
> > > Is the SB3048 a current boosting battery charger or a PV array max power
> > point
> > > device? I have 8 each 4-module series strings of Siemens SP70 modules
> > feeding
> > > into a C40 and then into a net metered SW4048 with a small backup battery
> > bank.
> > > The batteries just sit there (pulling the inverter off max power point),
> > but the
> > > net metered load is the grid so it can take all the PV I produce. Right
> > now
> > > (4:30PM) my C40 digital meter says 16 amps at 54 volts equals 864 watts.
> > Will I
> > > produce 19.2 amps at 54 volts or 19.2 amps at 45 volts with the SB3048?
> > >
> >
> > - - - -
> > To send a message: RE-wrenches at topica.com
> >
> > Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
> >
> > List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
> >
> > Check out participant bios: www.mrsharkey.com/wrenches/index.html
> >
> > Hosted by Home Power magazine
> >
> > Moderator: michael.welch at homepower.com
> >
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
==^================================================================
More information about the RE-Wrenches
mailing list